Page 1 of 3
Eastron SDM 630 Energy
Posted: 16 Jul 2023, 14:02
by frank
I'm working on connecting an Eastron SDM630 modbus version 2 to an ESPeasy with P078 on it. This doesn't really work for me. The main issue is that there are know readings from the SDM630 Can someone help me?
This is how i set the esp up with hw serial off in the advanced menu:
- Schermafbeelding 2023-07-16 134904.png (66.24 KiB) Viewed 75619 times
This is how the connections are
- setup.jpg (1.07 MiB) Viewed 75619 times
This is the setup of the eastron
- set adres.jpg (104.83 KiB) Viewed 75619 times
- set baud.jpg (109.31 KiB) Viewed 75619 times
- set pari.jpg (107.33 KiB) Viewed 75619 times
- set stop.jpg (105.2 KiB) Viewed 75619 times
Re: Eastron SDM 630 Energy
Posted: 16 Jul 2023, 14:32
by Ath
It might help if during boot you have the plugin disabled, and with a small delay, enable it from rules, like this:
on System#Boot do
TimerSet,1,10
on Rules#Timer=1 do
TaskEnable,Laadpaal
Rationale: During boot the serial port is enabled, and assigned to the serial console. After a few hundred milliseconds, the settings are read, where the Serial console gets turned off, but often the plugin(s) are already being initialized, where this task fails to initialize as the serial console is still using/blocking the serial port. After the boot process decouples the serial port, (re)initializing the task will succeed in claiming the serial port and gets properly initialized
Posted: 16 Jul 2023, 15:16
by TD-er
The picture of the baud rate is a bit unclear as the decimal dot (if any) isn't visible at this viewing angle.
So if there isn't a decimal dot, then you actually set it to 96000 baud.
This would be a really strange setting, but maybe you can verify there actually is a decimal dot, or the documentation mentions this situation?
Also the default serial port config would be something like "8N1", meaning No parity and 1 stop bit.
Posted: 16 Jul 2023, 15:20
by Ath
Both the RE and DE connections are combined on GPIO 12 (D6), not sure if that's on purpose?
Posted: 16 Jul 2023, 15:26
by TD-er
Ath wrote: ↑16 Jul 2023, 15:20
Yep, one is the inverse of the other
DE/RE where the / should be read as "overline"
Posted: 16 Jul 2023, 16:00
by frank
Ath wrote: ↑16 Jul 2023, 14:32
on System#Boot do
TimerSet,1,10
on Rules#Timer=1 do
TaskEnable,Laadpaal
That solved the booting issue. Thx did nothing for the not reading valuau's problem
Posted: 16 Jul 2023, 16:01
by TD-er
Have you looked at the "parity" setting?
I think that one might be wrong on your setup.
Posted: 16 Jul 2023, 16:02
by frank
TD-er wrote: ↑16 Jul 2023, 15:16
there is a decimal point between the 9 and the 6 so this is set to 9600 baud
Posted: 16 Jul 2023, 16:16
by frank
TD-er wrote: ↑16 Jul 2023, 16:01
i just tried every option (odd, even, none). No result
What should it be?
Posted: 16 Jul 2023, 16:20
by Ath
And swapping the RX and TX wires, does that help?
Posted: 16 Jul 2023, 16:31
by frank
Ath wrote: ↑16 Jul 2023, 16:20
just tried know difference
Posted: 16 Jul 2023, 20:11
by Ath
What release of ESPEasy is being installed on your ESP (the name is at the right-bottom of nearly every page of the Web-UI)?
Posted: 16 Jul 2023, 20:43
by frank
Ath wrote: ↑16 Jul 2023, 20:11
The latest release: Git Build: mega-20230623
Build: ESP_Easy_mega_20230623_energy_ESP8266_4M1M Jun 23 2023
Posted: 16 Jul 2023, 22:00
by TD-er
frank wrote: ↑16 Jul 2023, 16:16
What should it be?
It should be "None"
Posted: 16 Jul 2023, 22:02
by TD-er
Is "Enable Serial Port Console" unchecked on the Tools->Advanced page?
Posted: 17 Jul 2023, 06:22
by frank
TD-er wrote: ↑16 Jul 2023, 22:02
yes it is
Posted: 17 Jul 2023, 11:53
by TD-er
It looks like you're powering the MAX485 via 3V3.
Not all MAX485 chips work well at 3V3.
However you have the chip connected to the pins for Serial0.
These pins are also connected to the USB to serial chip on board.
I don't know if the MAX485 will output higher voltages on its TX pin when powered via 5V and if it does, whether you may damage the USB to serial chip.
Another thing you can try is to not let ESPEasy manage the DE/RE signal, but connect those pins all to the TX signal from the ESP.
Thus TX ESP to:
DI, DE, /RE
Posted: 17 Jul 2023, 17:41
by frank
TD-er wrote: ↑17 Jul 2023, 11:53
Thus TX ESP to:
DI, DE, /RE
Done both. Know change
Posted: 17 Jul 2023, 17:51
by frank
the only thing that strikes me is that I see the following in the device settings list:
Checksum (pass/fail): 0/768
Posted: 17 Jul 2023, 20:31
by Ath
frank wrote: ↑17 Jul 2023, 17:51
That just is an indication of the number of receive failures, versus the successes (0), so it seems there is some data received, but it doesn't seem decodeable by the plugin. It's possible that the SDM630 doesn't send a checksum, causing these errors.
Can you connect the RS485 board to a serial to USB adapter, and use some terminal software like Putty to see what's really being output by the SDM630?
The plugin also emits some logging when reading data, you can see what's going on via the Tools/Log page, you will see the data prefixed with EASTRON, so that should be easy to find.
Posted: 17 Jul 2023, 21:57
by frank
I have to look if i have such convertor. I will try tommorrow
thx for now
Posted: 17 Jul 2023, 22:16
by frank
could my problem be that my eastron SDM630 is a modbus V2?
Posted: 17 Jul 2023, 22:53
by TD-er
Isn't that "V2" just a revision of the meter itself and not the Modbus protocol?
And just to be sure, you do have a Modbus unit and not a version with M-Bus?
Posted: 17 Jul 2023, 22:56
by TD-er
There is a pending PR to extend the Eastron plugin to support all register types of all their meters.
I just updated the PR for it so it will generate a new test build.
In about 30 - 40 minutes a test build will be ready here:
https://github.com/letscontrolit/ESPEas ... 5580511157
Posted: 17 Jul 2023, 23:05
by frank
TD-er wrote: ↑17 Jul 2023, 22:53
In the meter stands modbus and not mbus so i think i have A modbus version. You can see that on the pictures.
by frank
Posted: 18 Jul 2023, 17:21
by frank
TD-er wrote: ↑17 Jul 2023, 22:56
I think the run didn't work well is see only bin's for the esp32 not for the esp8266
Posted: 18 Jul 2023, 21:29
by Ath
The build did fail, because of the bigger size of the added code.
I've created a local build with the LIMIT_BUILD_SIZE compile-time option enabled, so it will fit.
Here's the updated ESP8266 Energy build:
Posted: 19 Jul 2023, 18:46
by frank
I loaded the new bin. The esp is now rebooting every 2 minit. The reason is Exception (97) en the load is continues at 100%
PLUGIN_READ: timer, id: 0
Posted: 19 Jul 2023, 21:04
by TD-er
OK, I have to search for my Eastron modules... No idea in which box it will be...
Posted: 28 Jul 2023, 16:28
by PieterS
Ath wrote: ↑18 Jul 2023, 21:29
ESP_Easy_mega_20230718_energy_ESP8266_4M1M.zip
I flashed a ESP8266 NodeMCU with this code. It sends a SSID with the Energy but I have no idea about the password
And where can I find more info about this plugin?
Thnx
Posted: 28 Jul 2023, 16:37
by TD-er
Default password for the WiFi access point of the ESP is:
"configesp"
Posted: 28 Jul 2023, 17:18
by PieterS
@Gijs: Thanks.
Even when I select as Model Type the Eastron SDM630, the output is for a single fase meter.
Is there a change to get more detailed info for every fase? I want to send the data to Domoticz.
Posted: 28 Jul 2023, 19:45
by TD-er
There is a pending pull request to add all registers for all Eastron modules.
I merged in the latest changes and triggered a new build, which sould be ready in about an hour:
https://github.com/letscontrolit/ESPEas ... 5694781174
N.B. you need a GitHub account to download those GitHub Actions builds.
Posted: 28 Jul 2023, 19:58
by Ath
The current release version of the plugin in ESPEasy doesn't yet support all available data, but there is an open pull request on Github that aims to add those. The last build of that PR unfortunately failed, and that was because of a .bin size issue with the Energy build... guess that new build will also fail on that
I've created a local build of the ESP8266 Energy configuration, that I squeezed a bit by activating the LIMIT_BUILD_SIZE option, that limits a few features and removes debug-logging from ESPEasy, to make it fit in available .bin size:
Update via the Tools/Firmware Update button, and choose either the .bin or the .bin.gz file (that's a bit smaller to upload).
Posted: 28 Jul 2023, 21:41
by PieterS
TD-er wrote: ↑28 Jul 2023, 19:45
Thnx Gijs. I have a GitHub account and will give it a try tomorrow.
Posted: 28 Jul 2023, 21:48
by PieterS
Ath wrote: ↑28 Jul 2023, 19:58
ESP_Easy_mega_20230728_energy_ESP8266_4M1M.zip
Update successfull. Now I can choose lots of values. But next question: how do I send more than 4 values to Domoticz?
Posted: 28 Jul 2023, 21:57
by Ath
PieterS wrote: ↑28 Jul 2023, 21:48
ESPEasy only supports max. 4 values when sending from a task, but from rules you can send as many values as you want, you 'just' have to craft the json for Domoticz manually.
Alternative would be to configure multiple tasks with the SDM630 and send different values to different IDX devices of Domoticz. There's no way of sending 'the next 4 values' to Domoticz (not supported both by Domoticz and ESPEasy, as in technically impossible).
Posted: 29 Jul 2023, 15:39
by PieterS
I have the Modbus-version
Flashed the 8266 with the above version
made a rule for delay at boot
Connected the MAX485TTL to RS485 converter Module like @frank did in the start of this thread. Only difference is I powerd the module to Vin , not 3V3..
but did no success with reading the SDM630. Even swapped the wires between de module and the meter..
I can read the meter on a Raspberry Pi 4 connected by a RS485 to USB with settings on 9600 baud and a Python-script to send it to Domoticz. At that method I get the output I need but not very satisfied with that line-up.. I hope to go to MQTT. And a wireless solution.
This is part of the log in Domoticz from the Pythonscript:
Any idea why there is no input from the meter?
Posted: 29 Jul 2023, 16:35
by TD-er
How are the DE/RE pins wired?
Connected to the TX pin from the ESP?
How are RX and TX wired to the MAX485 module? Are you sure they aren't swapped?
How long is the cable from the MAX485 module to the Eastron?
Does the Eastron have a modbus address set?
Is serial config on the Eastron correct? (8N1 as in 8 bits, no parity, 1 stop bit)
You could also connect to the USB serial port of that module and connect to it using some terminal program like Putty as you should see what ESPEasy is sending. (set baud rate in that program to same baud rate as the Eastron module)
Just as a test, you could set the MAX485 module to other pins and use SW serial.
N.B. another user reported he now has lots of errors when using SW serial, but at least you should see some data being received in the task. Either the pass counter or the fail counter should increase.
Posted: 29 Jul 2023, 18:05
by PieterS
TD-er wrote: ↑29 Jul 2023, 16:35
Thnx Gijs for quick answers. I not a real technician so some words are not very familiar. Sorry if I misunderstand you. I will do my best.
I solderd RE and DE together.. And connected 1 wire to D6 on the ESP. Because Frank connected two wires to D6. No idea if that is meant as TX of the ESP..
EDIT at 19:35: Now I connect DI of the MAX485 module to pin TX (GPIO1) on the NedMCU and give it a new try. My source says: https://microcontrollerslab.com/rs485-s ... -tutorial/ Pin DI This is the driver input. It is connected with the TX pin of the microcontroller.
Edit at 19:49: No success either.
I disconnected the 2 wires between Eastron and RS485 2 USB. That system works OK. I checked before: D+=red cable D-=yellow cable. I connected the red cable (D+) to terminal block A, the yellow cable (D-) to terminal block B.
That works oke for RS485 to USB... But I changed the wires as a test earlier today. No luck.
How long is the cable from the MAX485 module to the Eastron? About 50 cm.
This is the situation with the RS485 to USB and Py. I disconnect the cable from RS485 and replace it to the MAX485 module.
I guess so. But I am not sure about it. This are the settings in Domoticz.. That does the job.
No idea about Stopbits and Parity. This meter is new and I did not change any settings in it.
I do not understand what you mean..
1. What pins are the USB serial port on the NodeMCU?
2. I have to connect them to a Raspberry Pi?
I found a diagram in this link:
https://www.industrialshields.com/blog/ ... module-137
Is that correct?
3. What command do I give in Putty?
Thanks for your effort to help me.
Pieter
Posted: 29 Jul 2023, 20:27
by TD-er
OK, that's a lot of uncertainties...
I advice you'll bookmark this table:
https://espeasy.readthedocs.io/en/lates ... on-esp8266
As it is a good guide on what pin can be used for what and which one has pull-up or -down resistors present etc.
Also it helps in translating this incredibly impractical D-notation into GPIO numbers.
I know some boards use this D-notation, but not all do.
So it only adds to the confusion.
Let's assume you have HW serial0 setup in the task in ESPEasy.
So GPIO-1 (TX) should then be connected to DI, DE/RE
GPIO-3 (RX) should be connected to RO of the MAX485 board.
If you have DE/RE not connected to the TX pin, but to another GPIO pin (e.g. GPIO-12 or D6 as you mentioned), you also need to set this in the task config for the DE/RE pin.
Since HW Serial0 is connected to the onboard USB to serial chip, you should be able to see the data sent by the ESP.
That's why I suggested to use some tool like Putty for this.
But if you never used such a tool, then forget it as it will only add to the confusion.
In your Domoticz screenshot the DeviceID is set to 1, so that should also be set in ESPEasy.
I don't know what the default settings are on the Eastron device, so you should look in the menu of the Eastron to make sure what serial port settings are set.
Also assuming defaults is also a bit tricky when debugging, so maybe a good idea to check this anyway.
No idea if Domoticz also might have changed some settings...
Posted: 30 Jul 2023, 13:03
by PieterS
TD-er wrote: ↑29 Jul 2023, 20:27
My board (Lolin NodeMcu V3) has a mixture..
Your suggestion for wiring looks different as the above from frank.
But I will give it a try.
In my Task Settings is selected: HW Serial0: GPIO-3 (D9) <- TX/ GPIO 1 (D10) -> RX
Sorry, I am not sure..
But I connect those
3 pins together on the RS485 module to one pin, TX-pin, on the NodeMCU??
and
I connect RO on the RS485 module to the RX-pin on the NodeMCU?
And of course 5V and GND.
We park the rest for later.
Thnx for your correction/confirmation.
Posted: 30 Jul 2023, 16:33
by TD-er
Yep, the DE and /RE (/ meaning it is electrically inverted) pins change communication direction on the RS485.
So you can join both DE and /RE and pull it down for listening and pull it up for sending.
If you assign a separate GPIO pin for toggling this, you have to set it in the task settings of course.
However, since the TX line of the ESP is "low" while not sending, you can just join the TX signal together with the data in and the DE/RE pins and achieve the same result.
N.B. there are use cases where this trick will not work, but for your setup I don't see why it shouldn't work.
Posted: 31 Jul 2023, 13:56
by PieterS
Sorry for delay. Thnx for information.
I checked the settings in te SDM630:
Did not find BIT-length in the Eastron....
This are Task Settings:
I joined DE and RE on the RS485 and connected them to the TX-pin of the NodeMCU.
I connect RO to the RX-pin
I tested this config, but no luck..
What about the DI on the RS485? Should it be connected? And to what pin on the NodeMCU?
Posted: 31 Jul 2023, 14:01
by TD-er
DI should be connected to the TX and you could then the DE/RE connect to GPIO-12 if you like.
So 2 options:
1) What you have right now, but also connect DE/RE to the DI pin (add some jumper to the pins on the other side of that board)
2) Disconnect the yellow wire from the TX and connect it to GPIO-12 (D6) and connect the TX to DI
I think the first option is the simplest to test right now.
Just short the 3 pins DI, DE, /RE
Posted: 31 Jul 2023, 14:40
by PieterS
Thnx Gijs,
I tried both options..
First the easy way with a jumper DI+DE/RE. No luck.
So the second option:
I removed the jumper
Yellow wire (DE+RE) to GPIO-12 (D6) and DI to TX.
No luck..
What else are my possibilities?
Posted: 31 Jul 2023, 14:50
by PieterS
What about Putty? I am familiar with SSH on a Raspberry..
Posted: 31 Jul 2023, 14:51
by TD-er
I assume you did connect the A/B line too and only had it disconnected for the picture?
What 'fail/success' values did you see on the web page?
On the previous page you at least showed there were some messages received, even though they were wrong.
I assume you have the serial log and serial console disabled on the tools->Advanced page.
I know there are some MAX485 chips out there that don't work well when powered by 3.3V (or not at all)
So you might want to power it via 5V, however since the USB to serial chip on the ESP board is also connected to the RX/TX pins of the ESP, I don't know what will happen to that chip when you power the MAX485 with 5V.
So maybe -just as a test- it is better to connect the DI and RO pins not to the RX/TX pins on the board, but rather use GPIO 5 (D1) and GPIO-4 (D2) and configure these as software serial port.
N.B. these pins are default configured for I2C, so make sure to remove them from the I2C config on the Hardware page.
I picked GPIO-5 and -4 as those are the ones not having any strange issues.
You can also pick GPIO-13 (D7), GPIO-14 (D5) and you already have GPIO-12 (D6) connected.
Posted: 31 Jul 2023, 16:05
by PieterS
Yes, I did.. I also connected power to the nodeMCU.
I think you mean the lines which start with EASTRON: (1,4)
Yes I did disabled that setting
In the tests of last Friday I had a NodeMCU with 5V on Vin. But that one is blown.. Now I use a Lolin. That has no 5V on Vin.. So I have no choice at the moment.. I orderd 2 new Amica's. Maybe I receive them tomorrow.
To be sure, I use a different (brandnew) MAX485 TTL to RS485 module (I have 2 of them) for the tests today.
The red light on the old one still works. But I am not sure.
But can you explain:
Thanks again.