Hi--
I have a MISOL WS2310 weather station that produces temp / humidity / wind / rain, and also UV and total light intensity.
This is the product:
http://www.misolie.net/misol-profession ... p-607.html
The temp / humidity / wind / rain part works great as "DKW2012" and all values are good.
However the UV and lux part does not. Instead it comes as an "Alecto V5" packet (rain and temperature). The values are "close" to the correct values, but not exactly. For Lux, I get lux-like values in the total rain field, but the values that wrap around (missing upper bits). The UV index data comes in the temperature field but is scaled weirdly. Also, the data is very sporadic, sometimes coming through for hours, sometimes not, suggesting a checksum/formatting check is failing when the bits are in certain ranges.
When I look at the following code for rtl_433
https://github.com/merbanan/rtl_433/blo ... t_wh1080.c
I see a similar layout. The temp / humidity / wind / rain come in msg_type == 0, and the UV + lux comes in msg_type == 2. But somehow RFLink is not parsing that third message type, and instead parsing as Alecto V5.
Can this be fixed?
Thanks,
Craig
Misol WS2310 / FineOffset / Alecto Lux & UV Values
Re: Misol WS2310 / FineOffset / Alecto Lux & UV Values
I would need to see debug data to fix the code.
see https://www.rflink.nl/develop.php
I did capture data in debug mode, and can confirm that this data is in "WH3080 UV/Light msg" format, as described in rtl_433 here,
but I think the timings are different. I did confirm that the other part of the weather stations reports, which show up as DKW2012 (temp, hum, wind, etc) is being reported correctly at the bit level.
I'll post a more full capture below, but basically the timing is
short=390us=1
long=1380us=0
(same as DKW2012) with 128 pulses. I then get samples of the following form
DARK
BRIGHT
I.e. in hex the format is
where
ff = preamble 0xff
T = sensor type = 0x7
II = sensor id = 0x01 in this case
U = UV index value = 0x0 in this case
55 = sensor OK = 0x55
LLLLLL = lux value (24-bit word)
CC = checksum
This is the same bit number and layout as described in rtl_433.
FULL DUMP ==============================================;; includes DKW2012 values which are sampled properly
$ miniterm.py /dev/tty.RFLink 57600
--- Miniterm on /dev/tty.RFLink 57600,8,N,1 ---
--- Quit: Ctrl+] | Menu: Ctrl+T | Help: Ctrl+T followed by Ctrl+H ---
20;00;Nodo RadioFrequencyLink - RFLink Gateway V1.1 - R48;
20;0B;RFDEBUG=ON;
20;2F;DEBUG;Pulses=128;Pulses(uSec)=300,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,6990;
20;30;Alecto V5;ID=0001;TEMP=813b;RAIN=0700;BAT=OK;
;;; 11111111 01110000 00010000 01010101 00000000 10101101 11000000 00000001
;;; f f TYPE{ id=1 }{UV} 55h=85OK {<---- LUX ------------->} {Chksum}
20;68;DEBUG;Pulses=176;Pulses(uSec)=300,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,390,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,390,6990;
20;69;DKW2012;ID=0001;TEMP=009b;HUM=44;WINSP=0018;WINGS=003d;RAIN=0018;WINDIR=0002;BAT=OK;
20;78;DEBUG;Pulses=128;Pulses(uSec)=270,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,390,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,1380,6990;
20;79;Alecto V5;ID=0001;TEMP=813b;RAIN=fb00;BAT=OK;
20;9C;DEBUG;Pulses=128;Pulses(uSec)=300,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,6990;
20;9D;Alecto V5;ID=0001;TEMP=813b;RAIN=e000;BAT=OK;
80,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,6990;
20;A7;DKW2012;ID=0001;TEMP=009a;HUM=45;WINSP=000c;WINGS=0025;RAIN=0018;WINDIR=0002;BAT=OK;
20;C6;DEBUG;Pulses=128;Pulses(uSec)=300,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,390,870,390,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,390,870,390,6990;
20;C7;Alecto V5;ID=0001;TEMP=813b;RAIN=da00;BAT=OK;
20;E1;DEBUG;Pulses=176;Pulses(uSec)=300,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,390,870,390,870,1380,6990;
20;E2;DKW2012;ID=0001;TEMP=0099;HUM=45;WINSP=0000;WINGS=0018;RAIN=0018;WINDIR=0002;BAT=OK;
20;EA;DEBUG;Pulses=128;Pulses(uSec)=300,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,390,6990;
20;EB;Alecto V5;ID=0001;TEMP=813b;RAIN=ce00;BAT=OK;
0,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,6990;
20;17;Alecto V5;ID=0001;TEMP=813b;RAIN=c500;BAT=OK;
20;21;DEBUG;Pulses=176;Pulses(uSec)=300,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,390,870,1380,870,390,870,1380,870,390,870,390,6990;
20;22;DKW2012;ID=0001;TEMP=009a;HUM=44;WINSP=0000;WINGS=0018;RAIN=0018;WINDIR=0002;BAT=OK;
20;37;DEBUG;Pulses=128;Pulses(uSec)=300,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,6990;
20;38;Alecto V5;ID=0001;TEMP=813b;RAIN=c500;BAT=OK;
20;58;DEBUG;Pulses=128;Pulses(uSec)=270,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,6990;
20;59;Alecto V5;ID=0001;TEMP=813b;RAIN=c500;BAT=OK;
20;7B;DEBUG;Pulses=128;Pulses(uSec)=270,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,6990;
20;7C;Alecto V5;ID=0001;TEMP=813b;RAIN=c500;BAT=OK;
20;83;DEBUG;Pulses=176;Pulses(uSec)=270,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,6990;
20;84;DKW2012;ID=0001;TEMP=0099;HUM=45;WINSP=000c;WINGS=0025;RAIN=0018;WINDIR=0002;BAT=OK;
20;9D;DEBUG;Pulses=128;Pulses(uSec)=270,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,390,870,390,870,1380,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,390,870,390,870,390,870,390,870,1380,870,1380,870,390,6990;
20;9E;Alecto V5;ID=0001;TEMP=813b;RAIN=a700;BAT=OK;
20;C1;DEBUG;Pulses=128;Pulses(uSec)=300,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,390,870,1380,870,390,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,390,870,390,870,390,6990;
20;C2;Alecto V5;ID=0001;TEMP=813b;RAIN=9800;BAT=OK;
20;C5;DEBUG;Pulses=176;Pulses(uSec)=240,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,390,6990;
20;C6;DKW2012;ID=0001;TEMP=0098;HUM=45;WINSP=000c;WINGS=0025;RAIN=0018;WINDIR=0002;BAT=OK;
20;E4;DEBUG;Pulses=128;Pulses(uSec)=300,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,6990;
20;E5;Alecto V5;ID=0001;TEMP=813b;RAIN=9500;BAT=OK;
20;04;DEBUG;Pulses=176;Pulses(uSec)=300,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,1380,870,390,870,390,870,390,870,390,870,390,6990;
20;05;DKW2012;ID=0001;TEMP=0098;HUM=45;WINSP=0000;WINGS=0018;RAIN=0018;WINDIR=0002;BAT=OK;
20;0D;DEBUG;Pulses=128;Pulses(uSec)=270,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,6990;
20;0E;Alecto V5;ID=0001;TEMP=813b;RAIN=8600;BAT=OK;
20;37;DEBUG;Pulses=128;Pulses(uSec)=270,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,390,870,390,6990;
20;38;Alecto V5;ID=0001;TEMP=813b;RAIN=7a00;BAT=OK;
20;3D;DEBUG;Pulses=176;Pulses(uSec)=300,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,1380,870,390,870,390,870,390,870,390,870,390,6990;
20;3E;DKW2012;ID=0001;TEMP=0098;HUM=45;WINSP=0000;WINGS=0018;RAIN=0018;WINDIR=0002;BAT=OK;
20;5B;DEBUG;Pulses=128;Pulses(uSec)=270,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,390,870,1380,6990;
20;5C;Alecto V5;ID=0001;TEMP=813b;RAIN=6e00;BAT=OK;
20;7D;DEBUG;Pulses=128;Pulses(uSec)=270,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,1380,870,1380,870,390,870,390,870,390,870,390,6990;
20;7E;Alecto V5;ID=0001;TEMP=813b;RAIN=6500;BAT=OK;
20;DB;DEBUG;Pulses=128;Pulses(uSec)=300,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,390,870,390,870,390,6990;
20;DC;Alecto V5;ID=0001;TEMP=813b;RAIN=5300;BAT=OK;
20;0A;DEBUG;Pulses=130;Pulses(uSec)=30,0,210,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,390,870,390,870,390,6990;
20;0B;Alecto V5;ID=0001;TEMP=813b;RAIN=5300;BAT=OK;
20;0E;DEBUG;Pulses=176;Pulses(uSec)=270,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,390,6990;
20;0F;DKW2012;ID=0001;TEMP=0096;HUM=45;WINSP=0018;WINGS=0049;RAIN=0018;WINDIR=0002;BAT=OK;
20;34;DEBUG;Pulses=128;Pulses(uSec)=270,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,390,870,390,870,390,6990;
20;35;Alecto V5;ID=0001;TEMP=813b;RAIN=4d00;BAT=OK;
20;4A;DEBUG;Pulses=176;Pulses(uSec)=270,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,6990;
20;4B;DKW2012;ID=0001;TEMP=0095;HUM=45;WINSP=0018;WINGS=0025;RAIN=0018;WINDIR=0002;BAT=OK;
20;5C;DEBUG;Pulses=128;Pulses(uSec)=270,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,1380,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,6990;
20;5D;Alecto V5;ID=0001;TEMP=813b;RAIN=3200;BAT=OK;
20;98;DEBUG;Pulses=128;Pulses(uSec)=270,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,390,870,390,870,390,6990;
20;99;Alecto V5;ID=0001;TEMP=813b;RAIN=2c00;BAT=OK;
20;A1;DEBUG;Pulses=176;Pulses(uSec)=240,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,390,870,1380,6990;
20;A2;DKW2012;ID=0001;TEMP=0094;HUM=46;WINSP=0000;WINGS=0018;RAIN=0018;WINDIR=0002;BAT=OK;
20;BD;DEBUG;Pulses=128;Pulses(uSec)=270,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,390,870,390,870,1380,870,1380,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,390,870,390,870,390,6990;
20;BE;Alecto V5;ID=0001;TEMP=813b;RAIN=1a00;BAT=OK;
20;E5;DEBUG;Pulses=128;Pulses(uSec)=300,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,390,6990;
20;E6;Alecto V5;ID=0001;TEMP=813b;RAIN=1400;BAT=OK;
20;08;DEBUG;Pulses=176;Pulses(uSec)=300,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,390,870,390,870,390,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,390,870,1380,870,390,870,1380,6990;
20;09;DKW2012;ID=0001;TEMP=0054;HUM=55;WINSP=000c;WINGS=0018;RAIN=0018;WINDIR=0004;BAT=OK;
20;B5;DEBUG;Pulses=128;Pulses(uSec)=240,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,6990;
20;B6;Alecto V5;ID=0001;TEMP=813b;RAIN=2403;BAT=OK;
;;; 11111111 01110000 00010000 01010101 00000001 00001100 00110100 00001010
... DARK
20;25;DEBUG;Pulses=128;Pulses(uSec)=270,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,390,870,390,870,390,870,1380,870,1380,870,390,6990;
20;26;Alecto V5;ID=0001;TEMP=813b;RAIN=0000;BAT=OK;
;;; 11111111 01110000 00010000 01010101 00000000 00000000 00000000 11111001
... FLASHLIGHT
20;4E;DEBUG;Pulses=128;Pulses(uSec)=270,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,1380,870,1380,870,390,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,390,6990;
20;4F;Alecto V5;ID=0001;TEMP=813b;RAIN=e200;BAT=OK;
20;02;DEBUG;Pulses=130;Pulses(uSec)=30,60,210,870,390,870,390,870,390,870,390,870,390,870,390,870,390,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,1380,870,390,870,1380,870,1380,870,390,870,390,870,390,870,1380,870,390,870,390,870,1380,870,1380,870,390,870,390,870,390,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,1380,870,390,870,390,6990;
20;03;Alecto V5;ID=0001;TEMP=813b;RAIN=ea03;BAT=OK;
;;; 11111111 01110000 00010000 01010101 00000001 01001110 11001110 00000011
short=390us=1
long=1380us=0
DARK
ff T I I U 55 L L L L L L C C
ff = preamble 0xff
CC = checksum
20;0B;RFDEBUG=ON;
... DARK
... FLASHLIGHT
Users browsing this forum: Bing [Bot] and 5 guests