I have a bunch of Marquant/Jula sensors that are picked up by the RFlink gateway. My problem is that I get 2 devices in domoticz for each sensor. One with temperature only and the other one with Temperature and Humidity. From the org. indoor unit I can only see the temperature of the remote sensor, no humidity.
I think my problem is that the humitidiy value gets discarded by the RFlink software as when received it doesn't look like a correct humidity value. The temperature is received OK it it alters between updating the device with temperature only and the one with temperature and humidity.
Is there any way to exclude the humidity in the readings so I only get 1 device in domoticz with temperature only?
Marquant/Jula Humidity
Re: Marquant/Jula Humidity
I think the RFlink software is interpreting the checksum as humidity.
I collected debugs from readings with and without humidity.
If I try to decode the pulses received from a reading the last 2 nibbles matches the humidity reading.
With humidity:
Without humidity:
Does it make sense? Could this be the problem?
20;12;DEBUG;Pulses=511;Pulses(uSec)=180,3780,390,870,390,1830,390,870,390,870,390,870,390,870,390,870,390,870,390,1830,390,870,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390,870,390,1830,390,870,390,1830,390,870,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390,1830,390,1830,390,870,390,870,390,1830,390,870,390,1830,390,1830,390,1830,390,390,390,3780,390,870,390,1830,390,870,390,870,390,870,390,870,390,870,390,870,390,1830,390,870,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390,870,390,1830,390,870,390,1830,390,870,390,870,390,870,390,1830,390,1830,420,1830,390,1830,390,1830,390,1830,390,870,390,870,390,1830,390,870,390,1830,390,1830,390,1830,390,390,390,3780,390,870,390,1830,390,870,390,870,390,870,390,870,390,870,420,870,390,1830,390,870,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390,870,390,1830,390,870,390,1830,390,870,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390,1830,390,1830,390,870,390,870,390,1830,390,870,390,1830,390,1830,390,1830,390,390,390,3780,390,870,390,1830,390,870,390,870,390,870,390,870,390,870,390,870,390,1830,390,870,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390,870,390,1830,390,870,390,1860,390,870,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390,1830,390,1830,390,870,390,870,390,1830,390,870,390,1830,390,1830,390,1830,390,360,390,3780,390,870,390,1830,390,870,390,870,390,870,390,870,390,870,420,870,390,1830,390,870,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390,870,390,1830,390,870,390,1830,390,870,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390,1830,390,1830,390,870,390,870,390,1830,390,870,390,1830,390,1830,390,1830,390,390,390,3780,390,870,390,1830,390,870,390,870,390,870,390,870,390,870,390,870,390,1830,390,870,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390,870,390,1830,390,870,390,1830,390,870,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390,1830,390,1830,390,870,390,870,390,1830,390,870,390,1830,390,1830,390,1830,390,390,390,3780,390,870,390,1860,390,870,390,870,390,870,420,870,390,870,390,870,390,1830,390,870,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390,870,390,1830,390,870,390,1830,390,870,390,870,390,870,390,1830,390,1830,390,1830,390;
20;13;Tunex;ID=4001;TEMP=80af;BAT=OK;
20;22;DEBUG;Pulses=511;Pulses(uSec)=150,3780,390,870,390,1830,390,870,390,870,420,870,390,870,390,870,390,870,390,1830,390,870,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390,870,390,1830,390,870,390,1830,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390,1830,390,1830,390,870,390,1830,390,870,390,870,390,1830,390,1830,390,1830,390,870,390,390,390,3780,390,870,390,1830,390,870,390,870,390,870,390,870,420,870,390,870,390,1830,390,870,390,870,390,870,390,1830,390,1830,420,1830,390,1830,390,870,390,1830,390,870,390,1830,390,870,390,870,390,1830,420,1830,390,1830,390,1830,390,1830,420,1830,390,870,390,1830,390,870,390,870,420,1830,390,1830,390,1830,390,870,390,390,390,3780,390,870,390,1830,390,870,390,870,390,870,390,870,390,870,390,870,390,1830,390,870,390,870,390,870,420,1830,390,1830,390,1830,390,1830,390,870,390,1830,390,870,390,1830,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390,1830,390,1830,390,870,390,1830,390,870,390,870,390,1830,390,1830,390,1830,390,870,390,360,390,3780,390,870,390,1830,390,870,390,870,390,870,390,870,390,870,390,870,390,1830,390,870,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390,870,390,1830,390,870,390,1830,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390,1830,390,1830,390,870,390,1830,390,870,390,870,420,1830,390,1830,390,1830,390,870,390,390,390,3780,390,870,390,1830,390,870,390,870,390,870,390,870,390,870,390,870,390,1830,390,870,390,870,390,870,390,1830,390,1830,390,1830,390,1830,420,870,390,1830,390,870,390,1830,390,870,420,870,390,1830,390,1830,390,1830,390,1830,390,1830,390,1830,390,870,390,1830,390,870,390,870,390,1830,390,1830,390,1830,390,870,390,360,420,3780,390,870,390,1830,390,870,390,870,390,870,390,870,390,870,390,870,390,1830,390,870,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390,870,390,1830,390,870,390,1830,390,870,390,870,390,1830,390,1860,390,1830,390,1830,390,1830,390,1830,390,870,390,1830,390,870,390,870,390,1830,390,1830,390,1830,390,870,390,360,390,3780,390,870,390,1830,390,870,390,870,420,870,390,870,390,870,390,870,390,1830,390,870,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390,870,390,1830,390,870,390,1830,390,870,390,870,390,1830,390,1830,390,1830,390,1830,390;
20;23;Tunex;ID=4001;TEMP=80ad;HUM=78;BAT=OK;
With humidity:
0100 0000 1000 1111 0101 0011 1111 0100 1110
0x4 0x0 0x8 0xF 0x5 0x3 0xF 0x4 0xE
HUM=78=0x4E which is the 2 nibbles above.
20;0F;Tunex;ID=4001;TEMP=80af;BAT=OK;
0100 0000 1000 1111 0101 0001 1111 1001 0111
0x4 0x0 0x8 0xF 0x5 0x1 0xF 0x9 0x7
Doing the same calculation here gives us HUM=0x97=151 which is invalid and probably discarded