I want to build a pulse counter for the S0 interface of three electricity meters. The counting of the pulses works already. Now I want to reproduce the current meter value via Rules.
My electricity meters emit 100 and 1000 pulses per kWh. The counted pulses must be divided by 100 or 1000 to calculate the actual meter value. Furthermore, I would like to calculate the meter reading to 1 decimal digit.
I have used "generic pulse counter" as devices. The variables count and total are filled accordingly.
Now I have created a rule that should do the calculation:
// Set the pulses per kWh per counter unit
On System#Boot do
  let,11,100 // Electricity meter 1: 100 pulses per kWh
  let,12,1000 // Current counter 2: 1000 pulses per kWh
  let,13,1000 // Current counter 3: 1000 pulses per kWh
// current total divided by pulses = meter value
// so that the meter value contains only one decimal digit
// round the quotient to (pulses per kWh) 10 and later divide by 10
on Pulse1#Total > 0 do
  let,1,round(Pulse1#Total/([int#12]/10))/10
on Pulse2#Total > 0 do
  let,2,round(Pulse2#Total/([int#12]/10))/10
on Pulse3#Total > 0 do
  let,3,round(Pulse3#Total/([int#13]/10))/10
Unfortunately the variables 1, 2 and 3 always remain at 0.
The devices are defined as:
Screenshot 2022-10-30 101114.png (110.21 KiB) Viewed 3048 times
What am I doing wrong?
Many greetings and thanks
Sepp
Interested layman ... ;)
Re: S0 Counter - Rules - calculate after new pulse
#2 Post by Ath » 30 Oct 2022, 10:52
You forgot a couple of square braces:
f.e. here
on Pulse1#Total > 0 do // The event doesn't have braces
  let,1,round([Pulse1#Total]/([int#12]/10))/10 // Accessing a variable requires square braces
spitzlbergerj
#3 Post by spitzlbergerj » 30 Oct 2022, 11:15
Thanks, @Ath,
I have now tried it with this:
on [Pulse1#Total] > 0 do
on [Pulse2#Total] > 0 do
  let,2,round([Pulse2#Total]/([int#12]/10))/10
on [Pulse3#Total] > 0 do
  let,3,round([Pulse3#Total]/([int#13]/10))/10
But the problem still exists ...
I show the variable on the display as follows
Screenshot 2022-10-30 111327.png (53.22 KiB) Viewed 3039 times
Var#11 is displayed correctly as 100 and all others are still displayed as 0
Any further ideas?
#4 Post by TD-er » 30 Oct 2022, 11:26
Can you show what is sent to the (debug) log?
Also not sure if it matters, but you can also just compute the value and then use formatting when showing it on the display.
let,1,[Pulse1#Total]/[var#12]
See for formatting:
https://espeasy.readthedocs.io/en/lates ... red-values
[var#1#D.1]
#5 Post by Ath » 30 Oct 2022, 11:30
spitzlbergerj wrote: 30 Oct 2022, 11:15 I have now tried it with this:
You have also added braces to the event (on .. do) line, but there you shouldn't have braces... :? (see comments in the example)
spitzlbergerj
#6 Post by spitzlbergerj » 30 Oct 2022, 11:54
Many thanks to you all,
here is the log:
1817352: EVENT: Pulse1#All=0,10021,0
1817392: EVENT: Pulse2#Count=0
1817396: EVENT: Pulse2#Total=45
1817401: EVENT: Pulse2#Time=0
1817432: EVENT: Pulse3#All=2,41,378
1818348: EVENT: Pulse1#All=0,10021,0
1818392: EVENT: Pulse2#Count=0
1818396: EVENT: Pulse2#Total=45
1818400: EVENT: Pulse2#Time=0
1818431: EVENT: Pulse3#All=0,41,0
1819350: EVENT: Pulse1#All=1,10022,5791
1819392: EVENT: Pulse2#Count=0
1819398: EVENT: Pulse2#Total=45
1819402: EVENT: Pulse2#Time=0
1819431: EVENT: Pulse3#All=0,41,0
1820408: EVENT: Pulse1#All=0,10022,0
1820412: EVENT: Pulse2#Count=0
1820415: EVENT: Pulse2#Total=45
1820423: EVENT: Pulse2#Time=0
1820441: EVENT: Pulse3#All=0,41,0
one more pulse at pulse counter 1
@Ath, sorry, I had tried it at the trigger first without [ ], that didn't work, so I added them brackets then.
Unfortunately the rule in both variants, i.e. trigger without brackets, does not work yet
@TD-er, unfortunately the simple statement without round doesn't work either.
spitzlbergerj
#7 Post by spitzlbergerj » 30 Oct 2022, 12:02
I have just found a solution. The following rule gets triggered and then also the correct calculation is done
on Pulse1#Time=0 do
  let,1,[Pulse1#Total]/[var#11]
Tahnks a lot for your help
Josef
#8 Post by TD-er » 30 Oct 2022, 12:32
Not sure whether the "=0" part should be there in the "on Pulse1#Time=0 do"
So keep an eye on that to see if keeps working as expected.
#9 Post by Ath » 30 Oct 2022, 12:38
You seem to have the setting "Single event with all values" checked for Pulse1, as there is a Pulse1#All event. That's not wrong, but if you enable that setting, the separate Pulse1#Count, Pulse1#Total and Pulse1#Time events won't be generated for that task, only that single Pulse1#All event, with all task values, comma separated and thus available as %eventvalue1%, %eventvalue2% and %eventvalue3% in the event.
Using the %eventvalue1% etc. arguments has the advantage that you receive the value at the moment the event was generated, instead of the current value when using the [taskname#value] variable, there can be a delay before the rule is processed, but the %eventvalue1% etc. values are kept with the event.
spitzlbergerj
#10 Post by spitzlbergerj » 30 Oct 2022, 13:02
Thank you, @Th-er and @Ath,
I will keep this in mind.
@Ath, I didn't understand fully the %eventvalue1%, %eventvalue2% and %eventvalue3% unfortunately. Could you explain it to me or link the doc for it.
And what would my rules look like then.
It would be great if I could update the rules for each event. Then I could also set the delay for the pulse counters higher.
And yes, I had the ALL option partially switched on. It is now off everywhere
Sepp
#11 Post by TD-er » 30 Oct 2022, 13:16
I think sending a single event with "All" values is the better option in this use case.
Like what Ton said, it has all 3 values from the same moment and it generated less events to process.
%eventvalue1% is the the first task value (Count)
%eventvalue2% is the second task value(Total)
%eventvalue3% is the 3rd task value (time)
on Pulse1#All do
  let,1,%eventvalue2%/[var#11]
#12 Post by Ath » 30 Oct 2022, 13:17
spitzlbergerj wrote: 30 Oct 2022, 13:02 @Ath, I didn't understand fully the %eventvalue1%, %eventvalue2% and %eventvalue3% unfortunately. Could you explain it to me or link the doc for it.
Documentation: https://espeasy.readthedocs.io/en/lates ... eventvalue
And please also look at the examples on that page (also above the paragraph that link takes you to)
spitzlbergerj
#13 Post by spitzlbergerj » 30 Oct 2022, 13:38
Oh, Yes, that's great. Thanks a lot
spitzlbergerj
Re: solved - S0 Counter - Rules - calculate after new pulse
#14 Post by spitzlbergerj » 01 Nov 2022, 08:48
Hi @Ath and @TD-er,
I have now tried around for a while. And it seems that the event
on Pulse1#All do
enddo
would not be recognized. Anyway no let command is executed
But if I set the trigger to
Pulse1#*
then it works.
Can this be?
#15 Post by Ath » 01 Nov 2022, 09:18
spitzlbergerj wrote: 01 Nov 2022, 08:48 I have now tried around for a while. And it seems that the event
on Pulse1#All do
enddo
Pulse1#*
then it works.
Can this be?
The <taskname>#All event is only generated if the corresponding checkbox is enabled for that task, if disabled, a separate event for each Value is generated.
Using "on Pulse1#* do" will catch any event for that task, including every Value event, or the All event if that's generated.
#16 Post by TD-er » 01 Nov 2022, 13:01
Please note that if you haven't checked to send all values in a single ....#All event, it will send as many events as there are task values for that task.