BME 280 wrong temp value
Trainer
#1 Post by Trainer » 04 May 2022, 19:28
i got wrong temp values from my BME280.
the temperature difference is +2°C.
How can i get more accurate data?
Re: BME 280 wrong temp value
#2 Post by Ath » 04 May 2022, 19:40
Often the sensor is mounted too close to an external heat source, that can be compensated by adjusting the 'Temperature offset' setting, in your case it should be -20.
Alternatively, if you need the original Humidity value (it may be correct, while the temperature is off), you can add this in the 'Formula' field of the 'Temperature' value: "%value%-2" (copy without the quotes).
Trainer
#3 Post by Trainer » 04 May 2022, 19:53
the sensor is in the shade in its own 3d printed housing in which only the sensor is located.
#4 Post by TD-er » 04 May 2022, 22:01
When using the temperature offset in the BME280, the humidity is also compensated for this offset.
So no need to compensate the humidity as this is absolutely NOT a linear relation.
The typical 2 degree offset was also an issue on some (really old) builds of ESPEasy.
This may happen when the registers of the BME280 were not all read in 1 single I2C transmission.
What build of ESPEasy are you running?
Trainer
#5 Post by Trainer » 04 May 2022, 22:33
i ue the last fw "ESP_Easy_mega_20220427_normal_ESP8266_4M1M".
i set the offset for 2°C but now after the temp is falling it is again wrong :(
#6 Post by Ath » 04 May 2022, 22:40
And that housing has enough openings so the temperature can (quickly) adjust to the surrounding ambient temperature?
#7 Post by TD-er » 04 May 2022, 22:54
Maybe also check the logs to see if you have read errors every now and then.
#8 Post by ThomasB » 05 May 2022, 01:42
I suggest posting a photo of your installed sensor. Photo should also show its placement from the ESP device.
#9 Post by TD-er » 05 May 2022, 09:30
And note the cable length!
Issues I've seen with the BME280:
- Reporting 2 degree too high (and thus humidity too low), on (really) old builds of ESPEasy
- Sensor heating itself, but that's less likely in a separate enclosure.
- Loose contacts or moisture shorting some pads => Check logs to see if there are faulty readings
- Too long I2C cabling, or missing pull-up resistors => lower I2C clock speed and check logs
Users browsing this forum: No registered users and 30 guests