Inputswitch state is deprecated
Moderators: grovkillen, Stuntteam, TD-er
Inputswitch state is deprecated
Hello there! I have this configuration, and get "Inputswitch state is deprecated" after swithing thermostat . What`s problem here?
- Attachments
-
- 2021-11-01 175651.jpg (244.04 KiB) Viewed 10358 times
-
- 2021-11-01 175724.jpg (210.47 KiB) Viewed 10358 times
-
- 2021-11-01 175742.jpg (165.58 KiB) Viewed 10358 times
-
- 2021-11-01 175804.jpg (56.33 KiB) Viewed 10358 times
Re: Inputswitch state is deprecated
First, you're missing an "endon" in your first rules block.
About inputswitchstate
I don't see it in your posted code/screenshots.
But I do see it in Domoticz MQTT controller code.
I looked at the code, but the only way I can see how this could occur is when there is some on your network is sending with IDX 0.
Still this should not happen and I need to fix it, but can you see if there is some device on your network sending to Domoticz using IDX 0?
About inputswitchstate
I don't see it in your posted code/screenshots.
But I do see it in Domoticz MQTT controller code.
I looked at the code, but the only way I can see how this could occur is when there is some on your network is sending with IDX 0.
Still this should not happen and I need to fix it, but can you see if there is some device on your network sending to Domoticz using IDX 0?
Re: Inputswitch state is deprecated
I will search. Thanks for endon!TD-er wrote: ↑01 Nov 2021, 13:38 First, you're missing an "endon" in your first rules block.
About inputswitchstate
I don't see it in your posted code/screenshots.
But I do see it in Domoticz MQTT controller code.
I looked at the code, but the only way I can see how this could occur is when there is some on your network is sending with IDX 0.
Still this should not happen and I need to fix it, but can you see if there is some device on your network sending to Domoticz using IDX 0?
Re: Inputswitch state is deprecated
There is no controller with IDX 0 which sending it to domoticz. I have 0 in several controllers but check is deactivateTD-er wrote: ↑01 Nov 2021, 13:38 First, you're missing an "endon" in your first rules block.
About inputswitchstate
I don't see it in your posted code/screenshots.
But I do see it in Domoticz MQTT controller code.
I looked at the code, but the only way I can see how this could occur is when there is some on your network is sending with IDX 0.
Still this should not happen and I need to fix it, but can you see if there is some device on your network sending to Domoticz using IDX 0?
Re: Inputswitch state is deprecated
I found a reason why i get this warning. I have 2 different devices (switch and MQTT Domoticz Helper) with the same idx=1. after removing idx from switch i get no warns! And it does`t matter if check was enable or disable, i`m still getting this error untill removed or set to 0!TD-er wrote: ↑01 Nov 2021, 14:03 I made an issue for this: https://github.com/letscontrolit/ESPEasy/issues/3829
Re: Inputswitch state is deprecated
I made some investigations and I have SonOff TX T3EUC2 flashed by 8285.normal ESPEasy. here is Devices, Rules and logs. If i Touch the button all ok, but if i tryied to switch from domoticz via MQTT i get this error in logs.This is only one way to make SonOff working properly.
Re: Inputswitch state is deprecated
Your rules could be somewhat more efficient:
The exclamation mark in front of the first argument to the event (%eventvalue1%) will invert the value (0->1 1->0).
(Edit: Changed %eventvalue1% to all lower-case)
Code: Select all
on Button1#State do
gpio,12,!%eventvalue1%
endon
on Button2#State do
gpio,5,%eventvalue1%
endon
(Edit: Changed %eventvalue1% to all lower-case)
Last edited by Ath on 04 Nov 2021, 15:26, edited 1 time in total.
/Ton (PayPal.me)
Re: Inputswitch state is deprecated
Button does`t reacting.Ath wrote: ↑04 Nov 2021, 12:18 Your rules could be somewhat more efficient:The exclamation mark in front of the first argument to the event (%eventvalue1%) will invert the value (0->1 1->0).Code: Select all
on Button1#State do gpio,12,!%EventValue1% endon on Button2#State do gpio,5,%EventValue1% endon
Re: Inputswitch state is deprecated
Not 100% sure the parsing of %eventvalue is case insensitive, so please try with lower case letters.
Re: Inputswitch state is deprecated
Ath wrote: ↑04 Nov 2021, 12:18 Your rules could be somewhat more efficient:The exclamation mark in front of the first argument to the event (%eventvalue1%) will invert the value (0->1 1->0).Code: Select all
on Button1#State do gpio,12,!%eventvalue1% endon on Button2#State do gpio,5,%eventvalue1% endon
(Edit: Changed %eventvalue1% to all lower-case)
Yep. THat Works. Thank You Ath and TD-er!
Last edited by Cdzn on 04 Nov 2021, 16:09, edited 1 time in total.
Re: Inputswitch state is deprecated
I edited my code to be lowercase, @Cdzn you might want to edit your quote as well, as you won't be able to change that in a couple of days (forum policy to avoid spammers changing their fake replies).
/Ton (PayPal.me)
Re: Inputswitch state is deprecated
Hi,
I've got the same message
and I'm not sure I understood if there was a resolution there
This is very serious because when it happened all the valves and the pump for the garden watering are switched on
Strangely it happens when I change the heater off my house!!!
I could not find yet what was in the common point (except: dz, LAN...)
The log
The rules
System Info
I've got the same message
Code: Select all
inputswitchstate is deprecatedinputSwitchState
This is very serious because when it happened all the valves and the pump for the garden watering are switched on
Strangely it happens when I change the heater off my house!!!
I could not find yet what was in the common point (except: dz, LAN...)
The log
Code: Select all
78786630: EVENT: Rules#Timer=6,1
78786857: ACT : Publish domoticz/in,'{'idx':1907,'nvalue':1,'svalue':'OK'}'
78786859: Command: Publish
78786860: Publish: domoticz/in{'idx':1907,'nvalue':1,'svalue':'OK'}
78786875: ACT : TimerSet,6,60
78786876: Command: TimerSet
78790160: EVENT: Rules#Timer=4,1
78790209: ACT : timerSet,4,5
78790210: Command: timerSet
78790213: ACT : gpio,13,0
78790214: Command: gpio
78790215: GPIO : port#13: set to 0
78794995: Command: inputSwitchState
78795000: inputswitchstate is deprecatedinputSwitchState,3,0.00
78795003: Command: inputSwitchState
78795008: inputswitchstate is deprecatedinputSwitchState,4,0.00
78795011: Command: inputSwitchState
78795016: inputswitchstate is deprecatedinputSwitchState,5,0.00
78795019: Command: inputSwitchState
78795024: inputswitchstate is deprecatedinputSwitchState,6,0.00
78795027: Command: inputSwitchState
78795032: inputswitchstate is deprecatedinputSwitchState,7,0.00
78795042: EVENT: Button1#State=1
78795286: ACT : Event,HandleButton=1,12,13
78795287: Command: Event
78795288: EVENT: HandleButton=1,12,13
78795653: ACT : AsyncEvent,OnOffRelay=1,0,13,1
78795654: Command: AsyncEvent
78795658: ACT : TimerSet,6,15
78795659: Command: TimerSet
78795663: ACT : TimerSet,7,1800
78795663: Command: TimerSet
78795667: ACT : Let,7,1
78795668: Command: Let
78795672: ACT : TimerSet,8,1200
78795673: Command: TimerSet
78795677: ACT : Let,8,1
78795677: Command: Let
78795682: ACT : Let,1,2
78795683: Command: Let
78796764: ACT : AsyncEvent,OnOffRelay=2,0,14,1
78796765: Command: AsyncEvent
78796769: ACT : TimerSet,6,15
78796770: Command: TimerSet
78796773: ACT : TimerSet,7,1800
78796774: Command: TimerSet
78796777: ACT : Let,7,1
78796778: Command: Let
78796781: ACT : TimerSet,8,1200
78796782: Command: TimerSet
78796785: ACT : Let,8,1
78796786: Command: Let
78796790: ACT : Let,2,2
78796791: Command: Let
78797300: EVENT: Rules#Timer=4,1
78797358: ACT : timerSet,4,5
78797359: Command: timerSet
78797362: ACT : gpio,13,0
78797363: Command: gpio
78797364: GPIO : port#13: set to 0
78797837: EVENT: Button3#State=0
78798090: ACT : Event,HandleButton=3,4,15
78798091: Command: Event
78798092: EVENT: HandleButton=3,4,15
78798449: Command: AsyncEvent
78798454: ACT : TimerSet,6,15
78798455: Command: TimerSet
78798458: ACT : TimerSet,7,1800
78798459: Command: TimerSet
78798462: ACT : Let,7,1
78798463: Command: Let
78798466: ACT : TimerSet,8,1200
78798467: Command: TimerSet
78798470: ACT : Let,8,1
78798471: Command: Let
78798475: ACT : Let,3,2
78798476: Command: Let
78798932: EVENT: Button4#State=1
78799310: ACT : gpio,15,=!1
78799312: Command: gpio
78799313: GPIO : port#15: set to 0
78799317: ACT : Let,4,2
78799317: Command: Let
78799321: ACT : TimerSet,9,3
78799322: Command: TimerSet
78799521: EVENT: Relay1#State=0
78800045: EVENT: Relay2#State=0
78800542: EVENT: Relay3#State=0
78801067: EVENT: Relay4#State=0
78801440: ACT : AsyncEvent,StopRelay123
78801441: Command: AsyncEvent
78801466: ACT : Publish domoticz/in,'{'command': 'customevent', 'event': 'aquaOnOffPump', 'data': 0}'
78801469: Command: Publish
78801470: Publish: domoticz/in{'command': 'customevent', 'event': 'aquaOnOffPump', 'data': 0}
78801600: EVENT: OnOffRelay=1,0,13,1
78801949: ACT : Let,5,(0-1)
78801950: Command: Let
78801957: ACT : Publish domoticz/in,'{'command': 'setuservariable', 'idx': 13, 'value': -1}'
78801960: Command: Publish
78801961: Publish: domoticz/in{'command': 'setuservariable', 'idx': 13, 'value': -1}
78801975: ACT : TaskValueSet 9,1,-1
78801976: Command: TaskValueSet
78801980: ACT : Let,5,abs(-1)*60
78801981: Command: Let
78801986: ACT : TimerSet,1,60
78801987: Command: TimerSet
78802166: EVENT: Relay1#State=1
78802702: EVENT: Relay4#State=1
78803096: ACT : AsyncEvent,StopRelay123
78803097: Command: AsyncEvent
78803122: ACT : Publish domoticz/in,'{'command': 'customevent', 'event': 'aquaOnOffPump', 'data': 0}'
78803124: Command: Publish
78803125: Publish: domoticz/in{'command': 'customevent', 'event': 'aquaOnOffPump', 'data': 0}
78803246: EVENT: Rules#Timer=9,1
78803590: ACT : Let,4,1
78803591: Command: Let
78803730: EVENT: Rules#Timer=4,1
78803781: ACT : timerSet,4,5
78803781: Command: timerSet
78803785: ACT : gpio,13,0
78803786: Command: gpio
78803787: GPIO : port#13: set to 0
78804294: EVENT: OnOffRelay=2,0,14,1
78804638: ACT : Let,5,(0-1)
78804639: Command: Let
78804646: ACT : Publish domoticz/in,'{'command': 'setuservariable', 'idx': 14, 'value': -1}'
78804649: Command: Publish
78804650: Publish: domoticz/in{'command': 'setuservariable', 'idx': 14, 'value': -1}
78804664: ACT : TaskValueSet 9,2,-1
78804665: Command: TaskValueSet
78804670: ACT : Let,5,abs(-1)*60
78804671: Command: Let
78804676: ACT : TimerSet,2,60
78804677: Command: TimerSet
78804853: EVENT: Relay2#State=1
78805360: EVENT: OnOffRelay=3,0,15,1
78805714: ACT : Let,5,(0-1)
78805716: Command: Let
78805724: ACT : Publish domoticz/in,'{'command': 'setuservariable', 'idx': 15, 'value': -1}'
78805726: Command: Publish
78805727: Publish: domoticz/in{'command': 'setuservariable', 'idx': 15, 'value': -1}
78805741: ACT : TaskValueSet 9,3,-1
78805742: Command: TaskValueSet
78805747: ACT : Let,5,abs(-1)*60
78805748: Command: Let
78805753: ACT : TimerSet,3,60
78805754: Command: TimerSet
78805936: EVENT: Relay3#State=1
Code: Select all
on Rules#Timer=4 do // status LED
if %iswifi% <7 do // wifi KO
timerSet,4,1
pulse,13,0,250
pulse,13,1,250
LongPulse_ms,13,0,250
elseif [Indicators#Heartbeat]=0 do // no heartbeat
timerSet,4,1
LongPulse_ms,13,1,500
elseif [AquaIndicators#TankLevelLow]=1 do // level Low
timerSet,4,2
LongPulse_ms,13,0,1300
else
timerSet,4,5
gpio,13,0 // OK
endif
endon
on AquaIndicators#TankLevelLow do // info from aquaMeter regarding the tank level
TaskValueSet 11,1,1 // KNOWN
TimerSet,5,180 // heartbeat
endon
on Rules#Timer=1 do
AsyncEvent,HandleRemainingTime=1,12,13
endon
on Rules#Timer=2 do
AsyncEvent,HandleRemainingTime=2,5,14
endon
on Rules#Timer=3 do
AsyncEvent,HandleRemainingTime=3,4,15
endon
on HandleRemainingTime do // relay, gpio, idx // calculate remaining time and publish to Dz
if [Durations#Relay%eventvalue1%]!=0
if [Durations#Relay%eventvalue1%]>60
Let,5,[Durations#Relay%eventvalue1%]-60
if [INT#5]>60
TimerSet,%eventvalue1%,60
else
TimerSet,%eventvalue1%,[INT#5]
endif
else
Let,5,0
gpio,%eventvalue2%,0
TimerSet,%eventvalue1%,0
endif
Publish domoticz/in,'{"command": "setuservariable", "idx": %eventvalue3%, "value": [INT#5]}'
TaskValueSet 9,%eventvalue1%,[INT#5] // update w remaining time
endif
endon
on DzTime1 do // event from Dz w the duration
AsyncEvent,SetDzTime=1,12,13,%eventvalue%
endon
on DzTime2 do
AsyncEvent,SetDzTime=2,5,14,%eventvalue%
endon
on DzTime3 do
AsyncEvent,SetDzTime=3,4,15,%eventvalue%
endon
on SetDzTime do // relay, gpio, idx, duration // set timer w the duration from Dz and publish to Dz
if %eventvalue4%<1800
Let,9,%eventvalue4%
else
Publish domoticz/in,'{"idx":1907,"nvalue":4,"svalue":"Duration for Relay%eventvalue1% from Dz too big: %eventvalue4%"}'
Let,9,60
endif
if [Relay%eventvalue1%#State]=0 and %eventvalue4%!=0
Publish domoticz/in,'{"command": "setuservariable", "idx": %eventvalue3%, "value": [INT#9]}'
if [Relay4#State]=0 // start the pump if off
gpio,15,1
endif
gpio,%eventvalue2%,1
TimerSet,%eventvalue1%,60
elseif [Relay%eventvalue1%#State]=1 and %eventvalue4%=0
Let,9,0
Publish domoticz/in,'{"command": "setuservariable", "idx": %eventvalue3%, "value": 0}'
gpio,%eventvalue2%,0
TimerSet,%eventvalue1%,0
endif
TaskValueSet 9,%eventvalue1%,[INT#9]
Let,%eventvalue1%,1 // unlock the button
endon
on AquaIndicators#WaterFlow do
if [AquaIndicators#WaterFlow]=0 then // no water
TimerSet,8,0
Let,8,0
if [INT#7]=0
TimerSet,7,1800
Let,7,1
endif
else
TimerSet,7,0
Let,7,0
if [INT#8]=0
TimerSet,8,1200
Let,8,1
endif
endif
endon
on Rules#Timer=5 do // no tank level received
AsyncEvent,StopAll=5
TimerSet,5,180 // to sync w aquaMeter
TaskValueSet 11,1,0 // UNKNOWN
if [INT#7]=0
TimerSet,7,600 // reset if no heartbeat
Let,7,1
endif
Let,7,1
if [INT#8]=0
TimerSet,8,600 // reset if no heartbeat
Let,8,1
endif
endon
on Rules#Timer=6 do // tank level: to check low if no heartbeat issue
if [AquaIndicators#TankLevelLow]=1 and [Indicators#Heartbeat]=1 do
AsyncEvent,StopAll=6
else
Publish domoticz/in,'{"idx":1907,"nvalue":1,"svalue":"OK"}'
endif
TimerSet,6,60 // next check of tank level
endon
on Rules#Timer=7 do
if [AquaIndicators#WaterFlow]=0 // No water used for a long time
AsyncEvent,StopAll=7
endif
TimerSet,7,1800
Let,7,1
endon
on Rules#Timer=8 do
if [AquaIndicators#WaterFlow]=1 // Water used too much
AsyncEvent,StopAll=8
endif
TimerSet,8,1200
Let,8,1
endon
on Button1#State do
Event,HandleButton=1,12,13
endon
on Button2#State do
Event,HandleButton=2,5,14
endon
on Button3#State do
Event,HandleButton=3,4,15
endon
on HandleButton do // relay, gpio, idx // the water valves
//LogEntry,'lock%eventvalue1%: [INT#%eventvalue1%]'
if [INT#%eventvalue1%]=1
if [Relay%eventvalue1%#State]=0
gpio,%eventvalue2%,1
if [Relay4#State]=0 // start the pump if off
gpio,15,1
endif
AsyncEvent,OnOffRelay=%eventvalue1%,0,%eventvalue3%,1
TimerSet,6,15 // reset next tank level check after opening the valve
TimerSet,7,1800
Let,7,1
TimerSet,8,1200
Let,8,1
Let,%eventvalue1%,2 // to lock until DzTime
else
gpio,%eventvalue2%,0 // no lock if Off because no return from dz expected
AsyncEvent,OnOffRelay=%eventvalue1%,0,%eventvalue3%,0
endif
elseif [INT#%eventvalue1%]=0 // after the boot
Let,%eventvalue1%,1
else
Let,%eventvalue1%,1+[INT#%eventvalue1%] // waiting for DzTime
if [INT#%eventvalue1%]>3
Let,%eventvalue1%,1 //if not message from dz, unlock the button after 3 times
endif
endif
endon
on OnOffRelay do // relay, gpio (0 if update done), idx, On(1)Off(0) // on or off the relay and publish to Dz
if %eventvalue2%!=0 // not already done
gpio,%eventvalue2%,%eventvalue4%
endif
Let,5,(0-%eventvalue4%) // => -1 a On ; 0 a Off
Publish domoticz/in,'{"command": "setuservariable", "idx": %eventvalue3%, "value": [VAR#5]}'
TaskValueSet 9,%eventvalue1%,[INT#5] // -1 Dz will give the duration: On DzTime
Let,5,abs([INT#5])*60
TimerSet,%eventvalue1%,[INT#5]
endon
on Button4#State do // the pump
if [INT#4]=1
gpio,15,=![Relay4#State]
Let,4,2 // to lock until DzRelay4 or Timer
TimerSet,9,3
else // after boot or unlock
Let,4,1
endif
endon
on Rules#Timer=9 do
Let,4,1 // unlock the button4
endon
on DzRelay4 do
gpio,15,%eventvalue1%
Let,6,1 // from dz directly
Let,4,1 // unlock the button
TimerSet,9,0
endon
on Relay4#State do
if [Relay4#State]=0
AsyncEvent,StopRelay123 // if the pump is turned off all relays are turned off
else
TimerSet,7,1800
Let,7,1
TimerSet,8,1200
Let,8,1
endif
if [INT#6]=0 // not from dz directly
Publish domoticz/in,'{"command": "customevent", "event": "aquaOnOffPump", "data": [Relay4#State]}'
else
Let,6,0
endif
endon
on StopRelay123 do // close all valves
if [Relay1#State]!=0
AsyncEvent,OnOffRelay=1,12,13,0
endif
if [Relay2#State]!=0
AsyncEvent,OnOffRelay=2,5,14,0
endif
if [Relay3#State]!=0
AsyncEvent,OnOffRelay=3,4,15,0
endif
endon
on StopAll do
if [Relay1#State]=1 or [Relay2#State]=1 or [Relay3#State]=1 or [Relay4#State]=1
gpio,15,0
AsyncEvent,StopRelay123
if %eventvalue1%=5
Publish domoticz/in,'{"idx":1907,"nvalue":4,"svalue":"No meters: stop!"}'
elseif %eventvalue1%=6
Publish domoticz/in,'{"idx":1907,"nvalue":4,"svalue":"Tank low: stop!"}'
elseif %eventvalue1%=7
Publish domoticz/in,'{"idx":1907,"nvalue":0,"svalue":"No water used for a long time: stop!"}'
elseif %eventvalue1%=8
Publish domoticz/in,'{"idx":1907,"nvalue":4,"svalue":"Water used too much: stop!"}'
endif
endif
endon
on System#Boot do
Let,1,0
Let,2,0
Let,3,0
Let,4,0
Let,5,0
Let,6,2
Let,7,1
Let,8,1
Let 9,0
gpio,12,0
gpio,5,0
gpio,4,0
gpio,15,0
TimerSet,4,1 // LED status
TimerSet,5,180 // aquaMeter heartbeat
TimerSet,6,15 // to check tank level
TimerSet,7,600 // no water flow for a long time
TimerSet,8,200 // water flow for too much time
if [Indicators#Booted]=0
TaskValueSet 11,2,1
Publish domoticz/in,'{"idx":1907,"nvalue":3,"svalue":"Cold restart"}'
else
Publish domoticz/in,'{"idx":1907,"nvalue":2,"svalue":"Reboot"}'
endif
endon
Code: Select all
Build:⋄
20112 - Mega
System Libraries:⋄
ESP82xx Core 2843a5ac, NONOS SDK 2.2.2-dev(38a443e), LWIP: 2.1.2 PUYA support
Git Build:⋄
Plugin Count:⋄
47 [Normal]
Build Time:⋄
Feb 23 2021 12:29:55
Binary Filename:⋄
ESP_Easy_mega_20210223_normal_ESP8285_1M
Build Platform:⋄
Linux-5.4.0-54-generic-x86_64-with-glibc2.29
Git HEAD:⋄
mega-20210223_9054eb3
Re: Inputswitch state is deprecated
Some screenshots
All Buttons are the same
All Relays are the same
Re: Inputswitch state is deprecated
@hestia, I don't have any advice on solving the reported problem. But I saw some syntax errors in your rules. Excerpt shown below, see the if and elseif statements that end in "do" (three places). This is incorrect usage, "do" is for event statements.
- Thomas
Code: Select all
on Rules#Timer=4 do // status LED
if %iswifi% <7 do // wifi KO
...
elseif [Indicators#Heartbeat]=0 do // no heartbeat
...
elseif [AquaIndicators#TankLevelLow]=1 do // level Low
...
Re: Inputswitch state is deprecated
Thanks Thomas for the review of the code.
Fixed, there was also a "then" at the end of an "if"!
No change for the problem
I still don't understand the link between what I do in dz (GUI + json to another server) and the trigger on the esp...
Fixed, there was also a "then" at the end of an "if"!
No change for the problem
Code: Select all
33337: WD : Uptime 1 ConnectFailures 0 FreeMem 23088 WiFiStatus 3 ESPeasy internal wifi status: Conn. IP Init
33580: EVENT: AquaIndicators#TankLevelLow=0
33620: ACT : TaskValueSet 11,1,1
33625: ACT : TimerSet,5,180
34085: EVENT: AquaIndicators#WaterFlow=0
34253: ACT : TimerSet,8,0
34254: TIMER: disable timer
34257: ACT : Let,8,0
35733: EVENT: Rules#Timer=4,1
35786: ACT : timerSet,4,5
35791: ACT : gpio,13,0
35793: GPIO : port#13: set to 0
40791: EVENT: Rules#Timer=4,1
40840: ACT : timerSet,4,5
40845: ACT : gpio,13,0
40847: GPIO : port#13: set to 0
44780: EVENT: Clock#Time=Wed,07:56
45845: EVENT: Rules#Timer=4,1
45892: ACT : timerSet,4,5
45897: ACT : gpio,13,0
45899: GPIO : port#13: set to 0
48671: inputswitchstate is deprecatedinputSwitchState,0,0.00
48679: inputswitchstate is deprecatedinputSwitchState,1,0.00
48687: inputswitchstate is deprecatedinputSwitchState,2,0.00
48695: inputswitchstate is deprecatedinputSwitchState,3,0.00
48703: inputswitchstate is deprecatedinputSwitchState,4,0.00
48712: inputswitchstate is deprecatedinputSwitchState,5,0.00
48720: inputswitchstate is deprecatedinputSwitchState,6,0.00
48731: inputswitchstate is deprecatedinputSwitchState,7,0.00
48773: EVENT: Button1#State=1
49053: ACT : Publish domoticz/in,'{'idx':1907,'nvalue':0,'svalue':'on Button1'}'
49313: EVENT: Button2#State=0
49566: ACT : Publish domoticz/in,'{'idx':1907,'nvalue':0,'svalue':'on Button2'}'
49822: EVENT: Button3#State=0
50110: ACT : Publish domoticz/in,'{'idx':1907,'nvalue':0,'svalue':'on Button3'}'
Re: Inputswitch state is deprecated
I've added a "security" to avoid all relays to open (to close them if opened in less than x seconds infact), but I'd like to understand what happened really and get a real fix.
I don't understand how the "inputswitchstate" could be "deprecated" as it is not connected to anything!
I don't understand how the "inputswitchstate" could be "deprecated" as it is not connected to anything!
Re: Inputswitch state is deprecated
As I mentioned, that command is sent from the Domoticz MQTT controller. See: viewtopic.php?p=55680#p55680
And the only way I could see it being created is if there is another unit on your network (may not even be an ESPEasy device) which is sending switch actions to the MQTT broker using IDX 0 or something using exactly the same IDX value as one of your switch tasks.
As far as I can see, it doesn't seem to do anything right now, other than generating log entries.
And the only way I could see it being created is if there is another unit on your network (may not even be an ESPEasy device) which is sending switch actions to the MQTT broker using IDX 0 or something using exactly the same IDX value as one of your switch tasks.
As far as I can see, it doesn't seem to do anything right now, other than generating log entries.
Re: Inputswitch state is deprecated
Thanks for your re reply
I better understand it. I had a lot of doubts on it because I didn't install mqtt anywhere except on dz and the esps for the watering!
But on the PI that trigger the issue, which is connected to my heater, I have vitalk, and I don't know exactly what is it
And I've found here https://github.com/mqu/viessmann-mqtt/w ... ation.main that it could be connected to mqtt (that I don't use)
Is it possible to have an hidden mqtt on my PI?
It triggers all the buttons of my device and so open all the valves of the water
Perhaps there was changed in a recent version? Mine: ESP_Easy_mega_20210223_normal_ESP8285_1M, and now that only put lines in the log?
I think it is more "IDX 0" that the exact IDX, because all the buttons of my esp are triggered!
Now that the root cause is known, how to fix it?
I'm not sure to be able to do anything on thes oft of my heater
I better understand it. I had a lot of doubts on it because I didn't install mqtt anywhere except on dz and the esps for the watering!
But on the PI that trigger the issue, which is connected to my heater, I have vitalk, and I don't know exactly what is it
And I've found here https://github.com/mqu/viessmann-mqtt/w ... ation.main that it could be connected to mqtt (that I don't use)
Is it possible to have an hidden mqtt on my PI?
Not at allit doesn't seem to do anything right now, other than generating log entries.
It triggers all the buttons of my device and so open all the valves of the water
Perhaps there was changed in a recent version? Mine: ESP_Easy_mega_20210223_normal_ESP8285_1M, and now that only put lines in the log?
I think it is more "IDX 0" that the exact IDX, because all the buttons of my esp are triggered!
Now that the root cause is known, how to fix it?
I'm not sure to be able to do anything on thes oft of my heater
Re: Inputswitch state is deprecated
follow up...
I'm not sure what do you mean by IDX... If it is this, I could put anything else as IDX just to avoid to have 0...?
I'm not sure what do you mean by IDX... If it is this, I could put anything else as IDX just to avoid to have 0...?
Re: Inputswitch state is deprecated
Yep.
The true bug here seems to be that there is no check whether that checkbox is checked.
I will make a commit for it, but for now you can type in any IDX value you don't use in Domoticz to see if that does improve your situation.
The true bug here seems to be that there is no check whether that checkbox is checked.
I will make a commit for it, but for now you can type in any IDX value you don't use in Domoticz to see if that does improve your situation.
Re: Inputswitch state is deprecated
Made a pull request for this: https://github.com/letscontrolit/ESPEasy/pull/3846
Please let me know what effect changing the IDX in that field has.
If it does help you with your issue, I can merge this PR as it will then fix this issue even with IDX set to 0.
Please let me know what effect changing the IDX in that field has.
If it does help you with your issue, I can merge this PR as it will then fix this issue even with IDX set to 0.
Re: Inputswitch state is deprecated
done!
9999x doesn't exist on dz, numbers big enough to stay like this
No longer "Inputswitch state is deprecated", so no unwanted watering
Nothing on dz side neither.
For that part, I think it's ok, thanks for your help
I'll do more testing for the whole system to be sure that everything is ok
I've put 9999x on all 8 first devices, possible w/o checking the checkbox.9999x doesn't exist on dz, numbers big enough to stay like this
No longer "Inputswitch state is deprecated", so no unwanted watering
Nothing on dz side neither.
For that part, I think it's ok, thanks for your help
I'll do more testing for the whole system to be sure that everything is ok